Home Forums Software FlexCase E Not Communicating over CAN

Viewing 10 reply threads
  • Author
    Posts
    • slkrugslkrug
      Participant
      Post count: 12

      I’m attempting to communicate with my Flexcase E for the first time. I have it connected to my machine via a Peak CAN device. I have a CAN 2 Lo (FCE J1-C3) and Hi (FCE J1-C4) pinned as per the datasheet. It was instructed to me to use these CAN channels by Amir.

      The attached error is occuring.

      Not sure if it matters or is related, but the toggle switch light on my harness has never turned on when connected to a computer and/or with Vbatt power.

      While following this (https://www.audesseinc.com/resources/flexcase-can-flasher/ ) tutorial, there has never been a 0.5sec beep from the buzzer when plugging in the PEAK CAN device through my CAN DB9 connector to pins C3 and C4.

      • This topic was modified 3 months ago by slkrugslkrug.
      Attachments:
      You must be logged in to view attached files.
    • ConnorConnor
      Keymaster
      Post count: 20

      – The diagnostic buzzer is not present on the FlexCase E, thank you for pointing out a mistake in the guide, I will fix promptly.

      – The error in your screenshot indicates that your computer does not recognize the peakCAN device. Did you install the peakCAN drivers mentioned in the Prerequisites for the tutorial?

      • slkrugslkrug
        Participant
        Post count: 12

        Thank you, looks like this was at least part of my problem. Will circle back later if I run into something else.

    • slkrugslkrug
      Participant
      Post count: 12

      I have verfied via a multimeter there is 12v going into connector pins Q1 and P1 from the battery source.

      There is continuity from pins FCE pin C3 (CAN HI) to DB9 Pin 7 and pin C4 (CAN LO) to DB9 Pin 2. This is the Audesse supplied CAN harness adapter.

      Attachments:
      You must be logged in to view attached files.
    • slkrugslkrug
      Participant
      Post count: 12

      Please see “No response” message in the attached image. The PEAK CAN drivers are all installed. Any ideas on how to fix and troubleshoot this one?

      • This reply was modified 3 months ago by slkrugslkrug.
      Attachments:
      You must be logged in to view attached files.
    • slkrugslkrug
      Participant
      Post count: 12

      Based on the notes in the tutorial, it seems like you have to flash it quickly after connecting. Got this error (attached). No clue what it means.

      Attachments:
      You must be logged in to view attached files.
    • ConnorConnor
      Keymaster
      Post count: 20

      Is the CAN bus terminated?

    • slkrugslkrug
      Participant
      Post count: 12

      If it’s not in the wiring harness/DB9 connector I got from you guys, then it’s not terminated. How can the harness be modified to include the termination, if you can reference the photos I attached above?

    • slkrugslkrug
      Participant
      Post count: 12

      Got a CAN termination circuit installed – now it worked. Thanks.

    • slkrugslkrug
      Participant
      Post count: 12

      I have flashed the 344 file for my FCE, as shown in the attached image.

      There are no CAN messages being received via PCAN view.

      Are there some settings required in PCAN view that aren’t mentioned anywhere in the tutorials for the messages to be broadcast? How can this one be troubleshooted?

      Attachments:
      You must be logged in to view attached files.
    • AmirFAmirF
      Moderator
      Post count: 25

      Could you confirm that you are writing to the same CAN that is connected to your PCAN device?
      I believe that for flashing software you are using CAN2(CAN2L->pin C3, CAN2H->C4). Can you confirm that the CAN write block you are using in your Simulink is also for CAN2?
      Also, please don’t remove the termination throughout the connection.
      Please see the attached image.
      Thanks,
      Amir

      Attachments:
      You must be logged in to view attached files.
    • slkrugslkrug
      Participant
      Post count: 12

      I’m flashing a .bin file from this tutorial, and trying to follow it exactly:

      I haven’t compiled anything from simulink yet.

      Can I not use this tutorial because I only have CAN2 set up? I confirm I have Can2L as pin c3 and Can2H as pin c4.

Viewing 10 reply threads
  • You must be logged in to reply to this topic.